Hello, reduce drastically the coef_int. Try 0.2 in your case. |
0 replies
22 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment



Uh oh!
There was an error while loading. Please reload this page.
I'm using a Sonoff TRVZB in two different rooms. In one of them, it takes very little time to reach the target temperature, but the room also cools itself down very quickly. This results in frequent opening/closing of the valve and overshooting the target temp as you can see in this graph. Setpoint is 20C from 1pm, 19C before as I was away and I'm using presence detection. I have another temp sensor directly on the radiator (Radiator Temperature):

Some overshooting (it reached 21.7C) is not an issue, but I'm wondering if/how it could do better and save some battery/wear on the TRVZB and maybe some gas. Maybe the valve could be open for longer but at a smaller percentage? Does it make sense?
I tried reducing coef_int and increase the cycle, but didn't see much difference. Thanks!
My config: