Hello, Your case seems to be a matter of valve tuning as explained here: https://www.versatile-thermostat.org/en/docs/self-regulation/#how-to-properly-adjust-the-parameters-that-control-the-opening Your valve is open at 15%: but the minimum opening to heat is set to a very low value: and so it is heating. First you have to fix some values:
Second you have to find the right values for your installation as explained in the link above:
|
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
I have a bunch of Sonoff TRVZB devices which I have setup with VT as over climate devices with direct control of valve regulation.
This is largely working fine but the TRVs are set with a hysteresis setting of -0.5C (has to be between -0.2 and -1 https://www.zigbee2mqtt.io/devices/TRVZB.html#temperature-accuracy-numeric)
which means that I am seeing the VTerm as heating (and therefore firing up the boiler) but the actual valve as idle


so real TRV shows as
whilst VTherm is
but the actual radiator is just sat there and ambient temperature means it isn't actually dropping low enough to kick back in and isn't warm. The boiler however has been on for an hour and a half making rooms without TRVs very hot when this the only TRV actually saying it needed heat.
What should the setup be to account for this?