TRV demand doesn't trigger boiler to switch on #783
Answered by
jmcollin78
Jan 7, 2025
Replies: 2 comments 4 replies
|
Hello, Before answering totally and fully read all your post, I don't understand the need of the Second, with Sonoff TRVZB, you should not configure the "closing degree" as explain here: https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/self-regulation.md#self-regulation-by-direct-valve-control If "closing degree" is configured, the hvac_action of the Sonoff TRV don't work and then VTherm can't know that the VTherm need for heat and don't activate the central boiler. You should first those 2 tips before going on further. |
4 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment




Yes it is better like this. Controling your central boiler with an
over_switchis really not a good idea because start and stop are constant.